Postby Tom Russell » Tue Jun 28, 2005 12:22 pm

System is a clutch recycling type
With A/C set to max cooling, air coming from dash outlets is 76 degrees
Ambient air is 90 degrees
Low side pressure cycles between 20-40 psi
High side pressure is 150 psi
There is a minor leak from the high side service port that I will repair when I figure out who borrowed my refrigerant recovery pump.
Ford service manual doesn’t cover adding refrigerant nor does it say anything about pressures.
Thank you.
Tom Russell
 

Undercharged

Postby Guest » Tue Jun 28, 2005 1:18 pm

You "appear" to be undercharged. At that ambinet, bring the high side up to around 200psi..Use only Virgin R134a and your cooling should return..Hope this helps.
Guest
 

Postby Tom Russell » Wed Jun 29, 2005 11:23 am

Thank you, I will give it a try.
Tom Russell
 